Hi,
I?m looking for some help/advice here. I work for an electric utility company in Arizona. I recently pulled some actual loads from a closed delta OH transformer bank. The transformer sizes are 50-100-50. I had a lineman perform a snap test for me to measure the amps on the secondary side. I took the high amps on each leg to calculate the load (KVA) on each transformer. I am having difficulty determining what portion of this load is 3-phase and what portion is 1-phase. The lighter transformer (commonly called pot in the utility industry) is the 100kVA transformer, and the power pots (2) are the 50kVAs. I used P=IE on each transformer using the AMPS from the snap test to see what the actual load is seen by each transformer (individually). For T1 (50kVA) I get 19kVA (by multiplying 240V by 78A); for T2 (100kVA) I get 40kVA (by multiplying 240V by 167A); for T3 (50kVA) I get 28kVA (by multiplying 240V by 117A).
My overall goal is to determine what portions of the loads seen by the transformer bank is single phase and what portion is three phase (where my difficulty is). With a Delta system (secondary side) the lighting transformers must be sized at 67% of the single phase load, and 33% of the three phase load (seen by T1 and T3). The power transformer is sized at 33% of the single phase load and 33% of the three phase load (see by T2). I?m trying to see if I can convert this bank to an OPEN DELTA system (one power transformer and one lighter transformer), but I?m not so sure what I need to do with the data collected to verify this. Please e-mail me your response at frank.greco@aps.com.
Thanks a million for the help,
Frank Greco
I?m looking for some help/advice here. I work for an electric utility company in Arizona. I recently pulled some actual loads from a closed delta OH transformer bank. The transformer sizes are 50-100-50. I had a lineman perform a snap test for me to measure the amps on the secondary side. I took the high amps on each leg to calculate the load (KVA) on each transformer. I am having difficulty determining what portion of this load is 3-phase and what portion is 1-phase. The lighter transformer (commonly called pot in the utility industry) is the 100kVA transformer, and the power pots (2) are the 50kVAs. I used P=IE on each transformer using the AMPS from the snap test to see what the actual load is seen by each transformer (individually). For T1 (50kVA) I get 19kVA (by multiplying 240V by 78A); for T2 (100kVA) I get 40kVA (by multiplying 240V by 167A); for T3 (50kVA) I get 28kVA (by multiplying 240V by 117A).
My overall goal is to determine what portions of the loads seen by the transformer bank is single phase and what portion is three phase (where my difficulty is). With a Delta system (secondary side) the lighting transformers must be sized at 67% of the single phase load, and 33% of the three phase load (seen by T1 and T3). The power transformer is sized at 33% of the single phase load and 33% of the three phase load (see by T2). I?m trying to see if I can convert this bank to an OPEN DELTA system (one power transformer and one lighter transformer), but I?m not so sure what I need to do with the data collected to verify this. Please e-mail me your response at frank.greco@aps.com.
Thanks a million for the help,
Frank Greco