This springs from the M-T-M post below. If you operate with an ATO (automatic throw over) scheme you temporally parallel both sides when transferring back to normal operation. For example double ended substation with a M-T-M configuration (tie normally open / closed transition) upon loss of L1 the tie breaker closes and L1 main opens, upon restoration of power to L1 and a 15 min. time delay to insure the utility distribution has stabilized the ATO transfers back to normal operation (L1 closed / Tie open / L2 closed) the ATO is set up for closed transition so for a incremeintal amount of time the substation is in closed transition. Should the bracing of the switchgear be reflected to accommodate the 2xSC for the duration of the closed transition? If the facility in question will be servicing the Xfmt1 so they closed transition the tie to de-energize X1 via closure of the tie and the opening of L1 when normal operation is restored via the ATO closed transition must the AIC account for 2xSC for the duration of the SC? We see installations all the time of ATS?s with closed trasition where under the closed transition (100ms or less) the available fault current may exceed the 35Kaic the switch is rated at? (the typically any c.b. rating of a closed transition overlapping neutral ATS 35Kaic in this example). Is there any standard to address this issue in a low voltage distribution or even medium voltage distribution or is it the responsibility of the Engineer sealing the drawings to make that decision? Your thoughts.:-?