A change in the last few code cycles allows identified LED or fluorescent fixtures in the closet zone where other fixture types are prohibited. This allows for among other things, lighted clothing rods.
 
Here is the Art.

410.16 Luminaires in Clothes Closets.


(A) Luminaire Types Permitted. Only luminaires of the following types shall be permitted in a closet:
(1) Surface-mounted or recessed incandescent or LED luminaireswith completely enclosed light sources
(2) Surface-mounted or recessed fluorescent luminaires
(3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the closet storage space


(B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.


(C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a closet storage space shall be as follows:
(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling.
(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling.
(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling.
(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling.
(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the closet storage space where identified for this use.
 
It is my thought that the intent of the code is to prevent a closet light that could become hot enough that should it come into contact with clothing it could start a fire.
As such the luminaries that are permitted by tje NEC and their method of installation makes sense.
 