410.8 tells us we may install a recessed fixture with a completely enclosed incandescent lamp 6" from the nearest point of storage. It also says if the fixture is surface mounted, the distance increases to 12".
Halo makes a trim which completely encloses the lamp, but it protrudes down out of the ceiling. Would a recessed fixture using this trim still qualify for the 6" rule?