I'd sit down and get real comfy with 410.8, look at the diagram, get a rock-solid footing about it.
The shower trim just gets you legally into the closet, it doesn't get you legally over the shelves.
If you're 6" off the shelf, a recessed can is perfectly legal. If he doesn't like it, show him the code and ask to see the local code that overrides it. I'd bet you 25? it ain't local code.NEC-2005 410.8(D) Location. Luminaires (fixtures) in clothes closets shall be permitted to be installed as follows:
(3) Recessed incandescent luminaires (fixtures) with a completely enclosed lamp installed in the wall or ceiling, provided there is a minimum clearance of 150 mm (6 in.) between the luminaire (fixture) and the nearest point of a storage space