Closet storage space

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
In Article 410.2 the definition says floor to height of 6ft or to the highest rod. My question is if the cieling is 8ft can you have a open recessed incandescent light ( can light ). 410.16 (B) says open or partially enclosed lamps not permitted but does not mention any height requirement.
 
Gus,

410.16 is giving permitted and not-permitted luminaires for closets, not storage space. Look at Article 100 for the definition, not 410.2.
 
In Article 410.2 the definition says floor to height of 6ft or to the highest rod. My question is if the cieling is 8ft can you have a open recessed incandescent light ( can light ). 410.16 (B) says open or partially enclosed lamps not permitted but does not mention any height requirement.

If this is a clothes closet you cannot have an open bulb incandescent anywhere in the space.
 