There is a cloths dryer at a clients house that is powered directly from the 200amp load center. #8-3 romex from a 30 amp 2p breaker to a four prong receptacle. When the dryer starts, lights dim a bit and the TV turns off but comes right back on. Checked the voltage, ground , neutral…. All the usual suspects.
I First went to the panel and checked the torque on all of the terminals including the main and neutral. Repaired a neutral crimp connector on the pig tail where it attached to the terminal strip on the dryer. Checked amperage on both legs. One jumped to 50 amps then settled at 20-22amps. The other leg had 0 at first but after 5-10 seconds showed 20 amps. Could something internally be causing this problem?
I First went to the panel and checked the torque on all of the terminals including the main and neutral. Repaired a neutral crimp connector on the pig tail where it attached to the terminal strip on the dryer. Checked amperage on both legs. One jumped to 50 amps then settled at 20-22amps. The other leg had 0 at first but after 5-10 seconds showed 20 amps. Could something internally be causing this problem?