They must all share a common grounding electrode system. 250.50. see 250.64(D) for how to connect multiple service enclosures to the grounding electrode system.If I have one transformer and am installing 3 meter/main combo enclosures can they all share a common set of ground rods? Or does each service need a dedicated set?
That is one possible option.Thanks, so one set for all three. Could I come off the closest rod with three acorns and a wire headed to each enclosure? I did read the code section, just trying to clarify what the best way to do this is.