Can CMR rated CAT6 cable be installed in gutters, flex, or conduit under an 18" raised floor that is used to supply environmental air? The area is office space, does not fall under 645. The communications contractor is installing this cable in a 17 story high rise. The installation is modular utilizing 4"x12" enclosed cable tray, 6"x6" screw cover gutter and flex. Article 800.53A and Table 800.53 list CMP cable. The communications engineer on the project stated that "plenum rated is only necessary if the cable is run exposed" and the present installation meets the code. The installed Type CMR cable is not exposed. Need your help guys.