Cnc machine disconnect needed?

Status
Not open for further replies.

Matt86

New User
Location
North carolina
Occupation
Industrial maintenance
Installing a new cnc machine that requires a transformer. Machine has a lockable disconnect for incoming power that turns everything off. The transformer will be hung less than 20 ft away. Is it necessary to put a disconnect between transformer and disconnect on machine?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
You need to look at the transformer secondary conductor rules in 240.21(C).
Remember the distances listed are for conductor lengths not the physical separation.
 
Status
Not open for further replies.
Top