Table 514.3(B)(2) lists electrical classifications for areas around CNG dispensers. 514.8 lists requirements for underground conduit installation for areas beneath the areas classified by 514.3(B)(2). And exception 2 allows for PVC conduit if buried 24" deep, provided certain requirements for ells and EGC are met. Concrete encasement of the UG PVC conduit is not required.
There are other area classifications for a CNG facility which are defined by NFPA 52 but are not referenced in article 514 (for instance 15' from compression equipment). Would the requirements/exception of 514.8 also apply to these areas? Or would UG conduit in these Class I Div 2 areas be required to meet 501.10(A), which references 501.10(A)(1)(a) exception, allowing PVC underground, but only if concrete encased.
In other words, does NEC require CNG station UG PVC conduit to be concrete encased in classified areas around CNG processing (vs. dispensing) equipment?
I am looking at the 2014 handbook, although I think these sections are unchanged from 2011.
There are other area classifications for a CNG facility which are defined by NFPA 52 but are not referenced in article 514 (for instance 15' from compression equipment). Would the requirements/exception of 514.8 also apply to these areas? Or would UG conduit in these Class I Div 2 areas be required to meet 501.10(A), which references 501.10(A)(1)(a) exception, allowing PVC underground, but only if concrete encased.
In other words, does NEC require CNG station UG PVC conduit to be concrete encased in classified areas around CNG processing (vs. dispensing) equipment?
I am looking at the 2014 handbook, although I think these sections are unchanged from 2011.