Hi
Please review the following and clarify
? Two Co gen sets 1500kVA @ 415V 50HZ supply operate in parallel with 3 x 1500kVA Utility power supply system.
? Utility supply is received at LV switchboard designed for a symmetrical short circuit current 53kA @ 1 sec.
? The two Co gen sets when running in parallel have a three phase symmetrical short circuit current of 40kA
? Utilty requires restricting the fault level at their switchboard to 53kA @ 1sec when operating in parallel
Question
Under parallel operation If there is a fault in Utility LV switchboard, the fault current contribution from the two Co gen sets has to be limited so that the magnitude of 53kA @ 1sec is not exceeded.
Please suggest a solution
Krishnan S
Question
Krishnan S