Okay, I'm getting my butt KICKED IN by question #8 on the Colorado JW Renewal Exam. Check it out:
8.) A plumbing pipe passing 66" above an indoor switchboard: (a) is permitted if a drip pan is installed over the switchboard. (b) is not permitted. (c) is only permitted above a suspended ceiling. (d) is permitted above NEMA 3R equipment
110.26 (F) (1) (a) basically says nothing can invade that space, INCLUDING "leak protection apparatus," thus eliminating (a) as an answer.
110.26 (F) (1) (b) basically contradicts (a). It says that foreign systems are okay if protection is installed to avoid damage to the electrical equipment.
I'm just blown away by this one.
Thanks,
Jason, The Power Connection INC.