Does the NEC require aluminum service entrance conductors at the main circuit breaker to be coated with an anti-oxidizing grease?
Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
They say an oxide inhibitor is recommended.Preparation of wire
When an aluminum cable is installed, certain
procedures should be followed to ensure a good connection.
1. The insulation should be stripped with a whittling motion to prevent the cable from being nicked.
2. The cable should then be cleaned with a wire brush. This removes the oxides from the surface of the conductor.
3. An oxide inhibitor (De-Ox) is recommended to be applied to aluminum conductor immediately prior to installation.
4. For mechanical connectors, the set screw should be tightened. After a few seconds, the set screw should be re-tightened to ensure a good connection. For compression connectors, the lug should be crimped around the conductor using the proper tool.