MURALS
Member
- Location
- SAN FRANCISCO
A 45KVA 3 phase transformer ( 480/208-120) has 70 amp primary protection. 150 amps Secondary breaker size in the panelboard which 3phase, 208/120, 4 wire, 100Amps. The panel is within 10 feet of transformer. Is this OK as per code? I think that the breaker size in the panel should be 100 Amps and not 150 Amps as the Panelboard is rated for 100 amps. Any comments?