Code article help

Therealcrt

Member
Location
Kansas City
Occupation
Electrician
I have looked and only found 313.17…

I’m trying to find where in the code if it’s a violation for a PVC conduit to enter the back of a metal box (1900 box) without using a PVC Connector. - full story the pvc is in a block wall with a stub 90 out at the top going into the back of a 1900 box but the stubs wouldn’t alow a connector to be put on and the box sit flush on the block wall. I know it’s a code violation but where does it say it
 

Therealcrt

Member
Location
Kansas City
Occupation
Electrician
I have looked and only found 313.17…

I’m trying to find where in the code if it’s a violation for a PVC conduit to enter the back of a metal box (1900 box) without using a PVC Connector. - full story the pvc is in a block wall with a stub 90 out at the top going into the back of a 1900 box but the stubs wouldn’t alow a connector to be put on and the box sit flush on the block wall. I know it’s a code violation but where does it say it
314.17*
 

Choice_Gorilla

Senior Member
Location
New England
Occupation
Journeyman Electrician
300.18 (a) says the raceway needs to be complete. It’s not complete without the connector to the box.

352.46 says you need a bushing or adapter to protect wire entering a box/enclosure
 