ken44
Senior Member
- Location
- Austin, TX
An electrical contractor just finished with a remodel at one of our commercial buildings, I cited a code violation where the contractor failed to use locknuts on a 3" nipple that goes between two panels. The project manager is asking me, on their behalf, if they can use a UL Listed Split Bushing with a Grounding Lug by Bridgeport. My stance is that while this is a UL Listed product, it is not a replacement for the locknuts, and the mechanical strength and bonding that they provide. Input please?