To reduce voltage drop, we must increase circuit wires from #12 to #6 AWG, the ground wire will be increase to #6 AWG per NEC 250.122(B) as well.
However, #6AWG conductor will be good for 65A (75 degree C conductor), and per table 250.122, #8 ground is needed not #6 as noted in NEC 250.122(B) rule above. Do these two code sections conflict?
However, #6AWG conductor will be good for 65A (75 degree C conductor), and per table 250.122, #8 ground is needed not #6 as noted in NEC 250.122(B) rule above. Do these two code sections conflict?