kanderson
Member
- Location
- Irving TX USA
Does anyone know the intention of the wording "Maximum Demand". Let's say I calculate my load in a panel schedule that calculates the connected load (just the VA) and the demanded load (VA * appropriate demand). In article 220.87 "Determining Existing Loads" (2) states "The maximum demand at 125% plus the new load does not exceed the ampacity of the feeder or rating of the service.
So now I apply another demand to my already demanded load or is that "double dipping" so to speak? ( the panel schedule automatically adds 125% to the lights, take the receptacle demand and so forth).
Thanks
Wire Nuts in Irving
So now I apply another demand to my already demanded load or is that "double dipping" so to speak? ( the panel schedule automatically adds 125% to the lights, take the receptacle demand and so forth).
Thanks
Wire Nuts in Irving