jcook980
Member
- Location
- Gresham, Oregon
- Occupation
- Electrical Engineer
Here is a very basic Code question from a well-known, highly regarded Electrical PE exam review book. I throughly and completely disagree with the published answer. Before I reveal their answer in a future post, you may wish to work through the problem yourself:
A 200 hp, 460V, three-phase, continuous duty, squirrel cage induction motor is designed to operate at a 0.85 power factor. The supplying branch circuit is 30.5m long and utilizes THHN copper conductors in a steel conduit. The voltage drop is limited to 3% in the branch circuit, leaving 2% for the feeder circuit. NEC Table 430-150 and Table 9 list the applicable data. What size cable should be used to meet the voltage drop and current requirements of the load?
What is your answer?
[ December 08, 2003, 12:58 PM: Message edited by: jcook980 ]
A 200 hp, 460V, three-phase, continuous duty, squirrel cage induction motor is designed to operate at a 0.85 power factor. The supplying branch circuit is 30.5m long and utilizes THHN copper conductors in a steel conduit. The voltage drop is limited to 3% in the branch circuit, leaving 2% for the feeder circuit. NEC Table 430-150 and Table 9 list the applicable data. What size cable should be used to meet the voltage drop and current requirements of the load?
What is your answer?