Well my situation is that behind a small building with a 400A 240v 3phase service,(and the building only using single phase of the 3phase service)with the meter mounted to the left of the aux.gutter and having 4 disconnects below the gutter.
Well my concern here is that to the left of the main disconnects(Both main disconnects being in the center)there is a 60A disconnect feeding an A/C unit and to the right of the mains there is a 60A disconnect that controls a set of air compressors.With that being established,is it a violation for both the 60A disconnects to be tapped from the line side of the main disconnect?That being the load side of the metercan.
And the other concern i have is that the A/C and the air comppressor are the 3phase 240v,while the mains feeding the panel are single phase 240/120v.The high leg comes from the meter can into the aux.gutter and both A/C and air comp.are tapped into the high leg.
I'm aware of the upto 6 diconnect rule in section 230 of the nec,but I'm not 100% sure of what is permissible as far what kind of load is allowed to be tapped.
Does the wording of the nec permits any kind of load whether it be an a/c or an outlet for that fact as long it is fused properly?
Shouldn't these loads come from the a circuit breaker in the main panel instead of being spliced in the aux gutter that feed the mains?
I understand about 230.82 about firepumps and other exceptions but that is for the supply side of the service.PLease clarify!!!!!!
Any and all answer would ba appreciated!!!
thx!!
Well my concern here is that to the left of the main disconnects(Both main disconnects being in the center)there is a 60A disconnect feeding an A/C unit and to the right of the mains there is a 60A disconnect that controls a set of air compressors.With that being established,is it a violation for both the 60A disconnects to be tapped from the line side of the main disconnect?That being the load side of the metercan.
And the other concern i have is that the A/C and the air comppressor are the 3phase 240v,while the mains feeding the panel are single phase 240/120v.The high leg comes from the meter can into the aux.gutter and both A/C and air comp.are tapped into the high leg.
I'm aware of the upto 6 diconnect rule in section 230 of the nec,but I'm not 100% sure of what is permissible as far what kind of load is allowed to be tapped.
Does the wording of the nec permits any kind of load whether it be an a/c or an outlet for that fact as long it is fused properly?
Shouldn't these loads come from the a circuit breaker in the main panel instead of being spliced in the aux gutter that feed the mains?
I understand about 230.82 about firepumps and other exceptions but that is for the supply side of the service.PLease clarify!!!!!!
Any and all answer would ba appreciated!!!
thx!!