Code question !

Status
Not open for further replies.

Marqueszx

Member
Location
NY
Occupation
Electrician
Guys anyone know if you can mix 2 different panels on the same pull box ?
Both panels are emergency can you add one box 12x12x6 and have conduits going to inside the panels from the box ?
Also anyone knows in what part of the books can i find a answer ?
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
So you have a pull box that will house conductors from two separate emergency sources? I think you are OK I don't see any issues.

I am sure I will get corrected if I am wrong.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
First, just to be sure, we are talking about circuits covered by Article 700. If all of the circuits are Article 700 circuits, I believe that 700.10(B) permits circuits from two different Article 700 sources to be in the same enclosure. However from a design point of view, I don't see it as a good idea. It sets up a case where a fault on one system could take out circuits from the other system.
 
Status
Not open for further replies.
Top