Guys anyone know if you can mix 2 different panels on the same pull box ?
Both panels are emergency can you add one box 12x12x6 and have conduits going to inside the panels from the box ?
Also anyone knows in what part of the books can i find a answer ?
 
So you have a pull box that will house conductors from two separate emergency sources? I think you are OK I don't see any issues.

I am sure I will get corrected if I am wrong.
 
First, just to be sure, we are talking about circuits covered by Article 700. If all of the circuits are Article 700 circuits, I believe that 700.10(B) permits circuits from two different Article 700 sources to be in the same enclosure. However from a design point of view, I don't see it as a good idea. It sets up a case where a fault on one system could take out circuits from the other system.
 