Having argument with GC as phase conductors shorted an caused a small fire.
Existing 208v 3P-40A breaker feeding a disconnect switch with 30A fuses for a food warmer. The existing wiring is #8's.
We had to relocate the kitchen warmer about 20' away to a temporary location. They wanted the disconnect relocated along with the warmer and a splice box where the disconnect was to extend the wiring to the new disconnect/warmer temp location.
We did not relocate the disconnect and left it in it's existing location and ran new wiring(#10's) from the load side of the disconnect to the new(temporary) location for the warmer.
We took the stance that the 40a breaker on the panel should have tripped. And also it would be a code violation to splice the existing #8's to #10's and run from splice box and extend them to the new temporary disconnect switch location. We said leaving the 30a fused disconnect in place and running #10' from the load side to the new warmer location was code compliant.
Does this make sense???
Existing 208v 3P-40A breaker feeding a disconnect switch with 30A fuses for a food warmer. The existing wiring is #8's.
We had to relocate the kitchen warmer about 20' away to a temporary location. They wanted the disconnect relocated along with the warmer and a splice box where the disconnect was to extend the wiring to the new disconnect/warmer temp location.
We did not relocate the disconnect and left it in it's existing location and ran new wiring(#10's) from the load side of the disconnect to the new(temporary) location for the warmer.
We took the stance that the 40a breaker on the panel should have tripped. And also it would be a code violation to splice the existing #8's to #10's and run from splice box and extend them to the new temporary disconnect switch location. We said leaving the 30a fused disconnect in place and running #10' from the load side to the new warmer location was code compliant.
Does this make sense???