Jim bradford
New User
- Occupation
- Ac and electric contractor
I’m also an air-conditioning contractor as well as an electrical contractor. We installed a package unit with an MOP of 70 and MCA of 54.6 . The home had number six wire run from the panel to the unit so we put a 60 amp breaker in the panel. The inspector failed me said it has to have a 70. I thought as long as my breaker was between MOP and MCA and the wire was sized correctly for the MCA I was good.