Would like to know were, in the code, it permits you to pipe on duct work to control devices like sensors and modulating motors for dampers
 
I don't know of any section that states you can not do so, and as, for the most part the NEC is a "permissive" Code, unless it's stated you can not do so, then it is allowed. 300.11 states raceways shall be securely fastened inplace and if that can be accomplished, I see no problem, especially if the raceway is connecting components associated with the duct.
Keep in mind I may have overlooked something.
 
Would like to know were, in the code, it permits you to pipe on duct work to control devices like sensors and modulating motors for dampers
AFAIK, the only NEC requirement for ducts is regarding in ducts [ref: 300.22], not on [the outside of] ducts.
 