G Gordon S. Member Location San Francisco, CA Nov 22, 2011 #1 Are you allowed to install a grounding electrode conductor in the same raceway as the primary feed conductors for a transformer?
Are you allowed to install a grounding electrode conductor in the same raceway as the primary feed conductors for a transformer?
Smart $ Esteemed Member Location Ohio Nov 22, 2011 #3 Gordon S. said: Are you allowed to install a grounding electrode conductor in the same raceway as the primary feed conductors for a transformer? Click to expand... There is no code which prohibits it.
Gordon S. said: Are you allowed to install a grounding electrode conductor in the same raceway as the primary feed conductors for a transformer? Click to expand... There is no code which prohibits it.
raider1 Senior Member Staff member Location Logan, Utah Nov 22, 2011 #4 Smart $ said: There is no code which prohibits it. Click to expand... Agreed, but make sure that you comply with 250.64(E) if the raceway containing the primary conductors is a metal raceway. Chris
Smart $ said: There is no code which prohibits it. Click to expand... Agreed, but make sure that you comply with 250.64(E) if the raceway containing the primary conductors is a metal raceway. Chris