Gien the rated load current for an air conditioner is 30 pampered a 50 ampere breaker will not hold the starting current. The maximum size breaker for branch circuit protection amperes
 
Gien the rated load current for an air conditioner is 30 pampered a 50 ampere breaker will not hold the starting current. The maximum size breaker for branch circuit protection amperes
For an A/C, you need to look at the MCA and MOCPD on the nameplate.
Search for "MCA" in your code cycle to find relevant articles.
If you choose the breaker size equal to Max OCPD and it still will not hold for starting you have excessive VD or a defective installation.
 
Last edited:
Gien the rated load current for an air conditioner is 30 pampered a 50 ampere breaker will not hold the starting current. The maximum size breaker for branch circuit protection amperes


Where have you looked for an answer so far, and why did you look there?

I'll give you two clues for key words you should be looking for - Air conditioning equipment and overcurrent protection, and maybe expand the meaning of overcurrent protection to include short circuit and ground fault protection.
 
To go along with GoldDiggers post, have you read through article 440?

Roger
 
The way I do these questions is that I look for a few items in the question and match them to something in the NEC. For instance a/c--would be a clue since art. 440 is for a/c units. Now that article is broken down into many parts. The next important part of the question is overcurrent protective device or branch circuit protection. This is a little tricky because you may not be familiar with the terms in the code. You need to look for the section- there are 7 in this article- that deals with branch circuit short circuit and ground fault Protection. This is considered your branch circuit protection.
 