i have a couple of question on a commerial building. (this is a church job).
Can i feed other recp from the bathroom circuit, i know i can't in dwellings but how about commerial.
Dishwasher, they want me to install a plug under the sink and then use SO cord to feed the dw. i'm thinking thats no longer legal but can't find it in the nec.
where in the code does it say you can use the 90 degree ampacity table when derating wire for 310-15 (b)
also if thats true then you can put 9 #12 thhn current carrying conductors in the same conduit ( #12 thhn 90 degee table ampacity 30 amp 310-15(b) 9 conductors 70% derating equals 21 amp right?)
thanks for your input
Can i feed other recp from the bathroom circuit, i know i can't in dwellings but how about commerial.
Dishwasher, they want me to install a plug under the sink and then use SO cord to feed the dw. i'm thinking thats no longer legal but can't find it in the nec.
where in the code does it say you can use the 90 degree ampacity table when derating wire for 310-15 (b)
also if thats true then you can put 9 #12 thhn current carrying conductors in the same conduit ( #12 thhn 90 degee table ampacity 30 amp 310-15(b) 9 conductors 70% derating equals 21 amp right?)