code Questions

Status
Not open for further replies.

m2oliva

Member
please answer a couple simple questions to end a disagreement between two electricians.Is there A maximum size conduit that can be used for branch circuiting?Is the maximum # of conductors allowed in any raceway 30 or the amounts listed in tables 9?also the maximum amount of 20 amp receptacles on a 20 amp circuit.Thank you
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: code Questions

A) No maximum size of conduit listed, but you have to derate for more than 3 current carrying conductors in the conduit. The 50% derating at the 10th current carrying conductor makes large raceways impracticable.
B) The maximum number of conductors is limited by Chapter 9, Table 1. Note again the derating issue.
C) In residential there is no code limit. In other occupancies you use the 180 va value to come up with a limit of 13 receptacles per 20 amp circuit.
Don

[ March 06, 2003, 07:28 PM: Message edited by: don_resqcapt19 ]
 

russ

Senior Member
Location
Burbank IL
Re: code Questions

These are out of the Chicago code book, but their the same in the NEC.

18-27-348.7. Size.
(b) Maximum. The maximum size of tubing shall be the 4-in. electrical trade size.

18-27-346.6. Size.
(b) Maximum. Rigid metal conduit larger than 6-in. electrical trade size shall not be used.

Russ

[ March 06, 2003, 08:55 PM: Message edited by: russ ]
 

johnpm

Member
Location
Georgia
Re: code Questions

C) According to table 220-3(b). A dwelling unit has a load of 3VA per square foot. So, a 20A breaker could supply 800 square feet.
3VA x 800sq.ft=2400VA/120V=20A. Then you would have to determine how many recepts were required
in this area. Is it kitchen or other area?
 