I am an electrical engineer working on justifying the replacement of some old electrical distribution equipment. I have found several code violations, but there are other issues here that don't "seem" right, but I can't pinpoint any specific violation.
Here's the scenario (and some pictures too)...
The main disconnect inside this particular buidling is being fed from a the main switchgear (a 600A fusible disconnect) underground with 600mcm (I think - the markings are gone) wire. The main is a fusible disconnect, fused at 400A - one of the three fuses is a renewable fuse. (By the way, this is a 480V system).
So far, so good. Then there are 8 taps off the main disconnect. There are 4 main lugs attached to the disconnect and an "extra" lug drilled above the main ones. The lug on the right rear is a 4/0 wire that is spliced in the cable tray to a #12, #2, #4, and 3/0 wires (big ugly bundle). The #12 feeds a motor circuit about 50 feet away. The others feed other panels on this same wall.
The lug on the right front and left rear each feed a 125A disconnect (2/0) wire) about 15 feet away. These disconnects each feed a 75HP Air compressor.
The lug on the left front feeds another 125A disconnect with 3/0 wire which in turn feeds two 30A disconnects with #6 wire. This same lug has 5 - #10 wires connected under the same screw. Two of these #10 wires (parallel feed) feed a 480V outlet about 50 feet away. Another two of the #10 wires feeds a 20A disconnect to a small heater. The fifth #10 wire feeds a 30A disconnect that in turn feeds 5 small motors (1HP).
The added lug is a #6 wire that feeds (daisy chained) two 15kVA transformers, which each feed a 125A, 120V lighting Panel.
One more detail. The main disconnect cannot be completely closed, so the dust in the factory completely covers the wires in the enclosure.
I've found violations in 240.21, 310.4 and 240.4. Thanks for your help.
Barbara
Here's the scenario (and some pictures too)...
The main disconnect inside this particular buidling is being fed from a the main switchgear (a 600A fusible disconnect) underground with 600mcm (I think - the markings are gone) wire. The main is a fusible disconnect, fused at 400A - one of the three fuses is a renewable fuse. (By the way, this is a 480V system).
So far, so good. Then there are 8 taps off the main disconnect. There are 4 main lugs attached to the disconnect and an "extra" lug drilled above the main ones. The lug on the right rear is a 4/0 wire that is spliced in the cable tray to a #12, #2, #4, and 3/0 wires (big ugly bundle). The #12 feeds a motor circuit about 50 feet away. The others feed other panels on this same wall.
The lug on the right front and left rear each feed a 125A disconnect (2/0) wire) about 15 feet away. These disconnects each feed a 75HP Air compressor.
The lug on the left front feeds another 125A disconnect with 3/0 wire which in turn feeds two 30A disconnects with #6 wire. This same lug has 5 - #10 wires connected under the same screw. Two of these #10 wires (parallel feed) feed a 480V outlet about 50 feet away. Another two of the #10 wires feeds a 20A disconnect to a small heater. The fifth #10 wire feeds a 30A disconnect that in turn feeds 5 small motors (1HP).
The added lug is a #6 wire that feeds (daisy chained) two 15kVA transformers, which each feed a 125A, 120V lighting Panel.
One more detail. The main disconnect cannot be completely closed, so the dust in the factory completely covers the wires in the enclosure.
I've found violations in 240.21, 310.4 and 240.4. Thanks for your help.
Barbara