Code Reference Needed

Status
Not open for further replies.

jason

Senior Member
Location
Georgia
I recently wired a detached workshop. 40 amp service. A maximum of 50 ft from house panel to workshop panel. I ran 8/3 with ground, bought a ground bar and mounted in panel to seperate ground and neutral. Inspector says I have to drive a ground rod. Where can I find this in code book. Thx, Jason.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Code Reference Needed

Jason, look at 250.32. Take note of each paragraph to see the different applications.

Roger

[ March 26, 2003, 06:27 PM: Message edited by: roger ]
 

amptech

Senior Member
Location
Indiana
Re: Code Reference Needed

250.50 tells us what, if available, shall be bonded together to form the grounding electrode system at each building or structure served. Where none of the items are available, one or more shall be installed and used. Check 250.52(A)(1) through (A)(6) for a list of suitable electrodes.
 

jason

Senior Member
Location
Georgia
Re: Code Reference Needed

OK all, all jokes aside, maybe I really should get a new code book I dont have a 250.50 either! I bought my code book from Hughes electrical supply, and I notice on the cover that their logo is actually printed onto the cover. My code book jumps from 250.190 Grounding Of Equipment to ARTICLE 280 Surge Arresters. The cover of the code book clearly states NEC 2002 Natiomal Electrical Code International Electrical Code Series. I paid like 45.00 for it. Did I get ripped off or what?? Like I said, all jokes aside, this is really pissing me off. Thx all for the replies
 

bphgravity

Senior Member
Location
Florida
Re: Code Reference Needed

I think you really must be still joking. Article 250 does end with 250.190. 250.32 is on page 102, and 250.50 is on page 104. :eek:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Code Reference Needed

Jason, do you have a page #70-102?

Roger
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Code Reference Needed

As Roger said

250.52 Two or More Buildings or Structures Supplied from a Common Service
(A)Grounding Electrode Where two or more buildings or Structures are supplied from a common ac service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (c). Where there are no existing grounding electrodes, the grounding electrode(s) required in Part III of this article shall be installed.
 

jason

Senior Member
Location
Georgia
Re: Code Reference Needed

yes, and i apologize for jumping to conclusions, i feel like an idiot, lol. maybe i shoulda spent more than 15 seconds looking for it, sry. thx
 

james wuebker

Senior Member
Location
Iowa
Re: Code Reference Needed

iwire, my code book 2002 NEC art. 250.32 states two or more buildings or structures supplied from a common service. Art 250.52 states grounding electrodes. Jason should be reading carefully art. 250.32.
Bye
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Code Reference Needed

Thanks Roger, I typed that whole thing carefully so as not to mislead anyone but I did not notice the typo. on the article number.
 