Can you use 2 seperate tandon breakers side by for 2 air conditioners 240v in NC. I have been told yes. But my understanding in the code and manufacturer is no.
Agree with the BR breakers, I believe there are tandem breakers that have that function, though.Electrically, yes, but codewise, no. There's no common internal or manual trip.
Would you need a common trip with no neutral, or 120V loads?Electrically, yes, but codewise, no. There's no common internal or manual trip.
I have seen them with tie bars but I don't believe internal trip was available.Agree with the BR breakers, I believe there are tandem breakers that have that function, though.
The two inner half-poles, yes.I have seen them with tie bars but I don't believe internal trip was available.
But then again how could it be......
But it doesn't have an internal common trip.Common trip tandem 2 pole
View attachment 2566597
Actually the pictured breaker is non-common trip, you can see the wording below the right handlesIn pictured inner 2 are a 240V 30A common, the 2 outer are 240V 20A common.
Good catch, but just to be clear they do make them with BOTH inner and outers common trip (but sounds like OP only needs one pair common trip)Actually the pictured breaker is non-common trip, you can see the wording below the right handles
Not that I'm aware of but that doesn't mean there isn't.Good catch, but just to be clear they do make them with BOTH inner and outers common trip (but sounds like OP only needs one pair common trip)
And I agree.Unless I read it wrong, 240.15 actually allows listed handle ties on line to line loads in most of our typical 120/208/240 wiring systems. I thought the code required an internal trip. Please someone correct me if I am wrong.
(B) Circuit Breaker as Overcurrent Device. Circuit breakers
shall open all ungrounded conductors of the circuit both
manually and automatically unless otherwise permitted in
240.15(B)(1), (B)(2), (B)(3), and (B)(4).
(2) Grounded Single-Phase Alternating-Current Circuits. In
grounded systems, individual single-pole circuit breakers rated
120/240 volts ac, with identified handle ties, shall be permitted
as the protection for each ungrounded conductor for line-to
line connected loads for single-phase circuits.
(3) 3-Phase and 2-Phase Systems. For line-to-line loads in
4-wire, 3-phase systems or 5-wire, 2-phase systems, individual
single-pole circuit breakers rated 120/240 volts ac with identi
fied handle ties shall be permitted as the protection for each
ungrounded conductor, if the systems have a grounded neutral
point and the voltage to ground does not exceed 120 volts.
Unless I read it wrong, 240.15 actually allows listed handle ties on line to line loads in most of our typical 120/208/240 wiring systems. I thought the code required an internal trip. Please someone correct me if I am wrong.
(B) Circuit Breaker as Overcurrent Device. Circuit breakers
shall open all ungrounded conductors of the circuit both
manually and automatically unless otherwise permitted in
240.15(B)(1), (B)(2), (B)(3), and (B)(4).
(2) Grounded Single-Phase Alternating-Current Circuits. In
grounded systems, individual single-pole circuit breakers rated
120/240 volts ac, with identified handle ties, shall be permitted
as the protection for each ungrounded conductor for line-to
line connected loads for single-phase circuits.
(3) 3-Phase and 2-Phase Systems. For line-to-line loads in
4-wire, 3-phase systems or 5-wire, 2-phase systems, individual
single-pole circuit breakers rated 120/240 volts ac with identi
fied handle ties shall be permitted as the protection for each
ungrounded conductor, if the systems have a grounded neutral
point and the voltage to ground does not exceed 120 volts.
Yes. And Yes.But, on an Air Conditioner is the Circuit Breaker actually considered the "Overcurrent Device" ? or is it the "Short Circuit Ground Fault" protection?
Why?If the circuit breaker feeding an air conditioner is actually considered the "Overcurrent" device, then I don't see how we could you ever size our wire to a motor load with integral overload protection smaller than the OCPD feeding it.
Yes. And Yes.
Why?
The short circuit ground fault protection is an overcurrent device.Because the rule for manually and automatically opening is for a circuit breaker used as an "overcurrent device"
On a motor load or air conditioner you're allowd to size your wire smaller because of the "overcurrent protection device" incorporated into the motor's overload, and, the circuit Breaker ahead of it actually then becomes the Short Circuit Ground Fault protection.
JAP>