Here are a few questions from a code test and also a code sample question
test that I am having trouble answering:
1-What is the demand factor for large appliances?
A-50
B-75
C-80
D-100
2-A 1' rigid metal conduit with 4 current carrying conductors is permitted to be filled up to _____ percent of it's capacity.
A-125
B-100
C-80
D-40
Key says 40, I think its 80 T310.15(B)(2)(a)
3-A restaurant has the following equipment: 1 16KW cook top, 1 8KW dishwasher, 1 5KW water heater, 1 3KW dough roller, 1 2KW exaust fan. Useing the optional calculation method for kitchen equipment, the MINIMUM service demand for these loads would be
A-42.5KW
B-34.5KW
C-28.1KW
D-23.8KW
I came up with 32KW?
4-An eight unit apartment is served by a 120/208 volt 3 phase 4 wire system. Each apartment has a 4.5KW single phase 120/208 volt dryer. What would be the MINIMUM service demand for these dryers?
A-40KW
B-36KW
c_24KW
D-21KW
I come up with 27KW?
5-How many square inches of an electrical metallic tubing conduit that is 18" long can be used for conductor fill?
A-0.141
B-0.181
C-0.272
D-0.454
This question doesn't make sense to me?
6-According to the NEC, a 1 1/4" deep 4" square metal box has a MINIMUM cubic inch capacity of how many cubic inches?
A-24
B-23
C-22
D-20
I come up with 18"?
7-Which of the following correctly indicates the phase rotation of a 3 phase 120/208 wye type system?
A-A-C-B
B-C-B-A
C-B-C-A
D-C-B-A
test that I am having trouble answering:
1-What is the demand factor for large appliances?
A-50
B-75
C-80
D-100
2-A 1' rigid metal conduit with 4 current carrying conductors is permitted to be filled up to _____ percent of it's capacity.
A-125
B-100
C-80
D-40
Key says 40, I think its 80 T310.15(B)(2)(a)
3-A restaurant has the following equipment: 1 16KW cook top, 1 8KW dishwasher, 1 5KW water heater, 1 3KW dough roller, 1 2KW exaust fan. Useing the optional calculation method for kitchen equipment, the MINIMUM service demand for these loads would be
A-42.5KW
B-34.5KW
C-28.1KW
D-23.8KW
I came up with 32KW?
4-An eight unit apartment is served by a 120/208 volt 3 phase 4 wire system. Each apartment has a 4.5KW single phase 120/208 volt dryer. What would be the MINIMUM service demand for these dryers?
A-40KW
B-36KW
c_24KW
D-21KW
I come up with 27KW?
5-How many square inches of an electrical metallic tubing conduit that is 18" long can be used for conductor fill?
A-0.141
B-0.181
C-0.272
D-0.454
This question doesn't make sense to me?
6-According to the NEC, a 1 1/4" deep 4" square metal box has a MINIMUM cubic inch capacity of how many cubic inches?
A-24
B-23
C-22
D-20
I come up with 18"?
7-Which of the following correctly indicates the phase rotation of a 3 phase 120/208 wye type system?
A-A-C-B
B-C-B-A
C-B-C-A
D-C-B-A