I had a customer the other day ask me if he could attach his 3000W Honda 120V generator to a manual transfer switch. Yes, they do sell L5-30P to L14-30R adapters, but I'm not sure they are UL listed. Anyway, I was installing the switch and one of the circuits the HO selected was a MWBC. In the past when I've encountered this, I've been careful to move both hots to the transfer switch. I then realized that if that circuit was run on the generator, that the both legs would be in phase and overload the neutral. In this case, I told the HO that the MWBC could not go on the TS.
So, is this a NEC violation (I can't think of one) or a hazard not covered by the NEC or neither?
Thanks,
Mark