Cat 5 computer wiring does not typically require conduit for protection.
Since you are doing this work do you have a code book to refer to
However is this test pit in a classified or hazardous location?
 

webman.sm

Member
Location
Tulsa, Oklahoma, United States
Occupation
Industrial maintenance technician
Cat 5 computer wiring does not typically require conduit for protection.
Since you are doing this work do you have a code book to refer to
However is this test pit in a classified or hazardous location?
No, it's not in a hazardous location. I said the same thing about the need for conduit, and the mechanical engineer said it has to have it.

For some reason this company absolutely refuses to buy us a copy of NFPA70/NEC to have on hand. Will throw a fit over codes, but will want us to run EMT across the floor or down the walls at waist height.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
No, it's not in a hazardous location. I said the same thing about the need for conduit, and the mechanical engineer said it has to have it.

For some reason this company absolutely refuses to buy us a copy of NFPA70/NEC to have on hand. Will throw a fit over codes, but will want us to run EMT across the floor or down the walls at waist height.
Those are subjective calls as to if the EMT is exposed to physical damage. Of course the floor may be a tripping hazard, but the code does not care about that issue.
 

webman.sm

Member
Location
Tulsa, Oklahoma, United States
Occupation
Industrial maintenance technician
Those are subjective calls as to if the EMT is exposed to physical damage. Of course the floor may be a tripping hazard, but the code does not care about that issue.
I've always been told, if it can get damaged, it will get damaged. So I've always referenced 358.12 in those cases.


In this instance, the emt is ran against the stringer and as tight to the wall as possible. Stated it was a trip hazard, and violated codes. But couldn't tell me what codes.

Local company told them they wouldn't run it through the landing and I believe that is correct, and it was misconstrued as through the riser space.

This is the same engineer that wanted a threshold cut out of a tornado shelter because someone stubbed a toe on it. It's a 1/4" thick threshold. Manufacturer stated it would void all certifications.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
No, it's not in a hazardous location. I said the same thing about the need for conduit, and the mechanical engineer said it has to have it.

For some reason this company absolutely refuses to buy us a copy of NFPA70/NEC to have on hand. Will throw a fit over codes, but will want us to run EMT across the floor or down the walls at waist height.
You can view it for free at nfpa.org/70
 