Someone sent me a picture of this load center for a 1400 sq. ft. condo and was asking ME to point out any code violations.
Here's the ones I could find.
1. Electrical Tap over blank space.
2. Possible overload of panel with split type breakers. He didn't take a picture of the actual amperage rating of the load center bus but is going
try to find out.
3. Possibly imcompatibility of using square D, Cutler Hammer breakers
on a Challenger load center.

Does anyone else see any other code violations?
Thanks.
 
The panel is suitable for twin breakers and I would guess that it is a 125 amp loadcenter. I have no idea what it is fed with so I am not sure of any other violations.
 
john37 said:
Someone sent me a picture of this load center for a 1400 sq. ft. condo and was asking ME to point out any code violations.
Here's the ones I could find.
1. Electrical Tap over blank space.
2. Possible overload of panel with split type breakers. He didn't take a picture of the actual amperage rating of the load center bus but is going
try to find out.
3. Possibly imcompatibility of using square D, Cutler Hammer breakers
on a Challenger load center.

Does anyone else see any other code violations?
Thanks.
Sure looks like that buss got hot where the tape was covering!
Panel door says use only Sylvania or Challenger breakers.
Unless there is a main in front of the panel it violates 6 throws of the hand rule.
 
Last edited:
I didn't notice the breakers but it could be those Sq. D's are listed for theat panel. I know Seimens makes breakers that are listed for Sq. D. Now I am not sure how that works.... they fit and we are told they are listed.. but
 