E eddy212 Member Feb 21, 2006 #1 I KNOW ABOUT THE 180VA RULE , DOES THIS RULE APPLY IN A HEALTH CARE FACILITY, CAN I PUT 13RECEPTACLES IN A 20 AMP CIRCUIT.
I KNOW ABOUT THE 180VA RULE , DOES THIS RULE APPLY IN A HEALTH CARE FACILITY, CAN I PUT 13RECEPTACLES IN A 20 AMP CIRCUIT.
rcarroll Senior Member Location Fort Collins, Colorado Feb 21, 2006 #2 Re: code Yes the 180va code applies to health care. Yes you can put 13 receps on 1 20 amp ckt. Please turn off the caps when posting.
Re: code Yes the 180va code applies to health care. Yes you can put 13 receps on 1 20 amp ckt. Please turn off the caps when posting.