Would anybody know off hand what the coil burden would be for a 30 amp 2 pole lighting contactor? 120volt coil. I have a situation where I've got 18 contactor's located in a enclosure all controlling exterior lighting on a large property.
All lights can turn on and off at the same time.Currently there are several 7 day time clocks that only provide coil activation to the contactor's and the owner does not want the hassle of constantly resetting these mechanical behemouths. Past owner had a wide variety of on/off settings that are now not needed. If applicable I would propose using 1 inexpensive Intermatic spst clock to handle all.
 
Would anybody know off hand what the coil burden would be for a 30 amp 2 pole lighting contactor? 120volt coil. I have a situation where I've got 18 contactor's located in a enclosure all controlling exterior lighting on a large property.
All lights can turn on and off at the same time.Currently there are several 7 day time clocks that only provide coil activation to the contactor's and the owner does not want the hassle of constantly resetting these mechanical behemouths. Past owner had a wide variety of on/off settings that are now not needed. If applicable I would propose using 1 inexpensive Intermatic spst clock to handle all.
Did you consult with the contactor manufacturer? I know that the manufacturers that I had worked for included this information as part of the catalog specifications.
 
I agree with templdl. Coil load varies with make and model.

But I will guess the burden is less than one amp per contactor... :D
 
Should be fine. If your coils draw too much you could always use the the digital timer to trigger a control contactor or a 120v relay.
 
Should be fine. If your coils draw too much you could always use the the digital timer to trigger a control contactor or a 120v relay.
Even if they don't draw too much steady-state current, the inrush required may be too much for the circuit impedance.
But better not to have all 18 of them pull in at the same time.
In this case may have to install two timers with slight timing disparity, or use a time-delay ON relay to trigger a portion of them.
 
But better not to have all 18 of them pull in at the same time.

McMaster-Carr as well as many other sources offer two terminal timers you can put in series with the coil, offering time delays from a fraction of a second up to several minutes. With a few of these you can have one master timer operate all lights but have them come on in sequence.
 
McMaster-Carr as well as many other sources offer two terminal timers you can put in series with the coil, offering time delays from a fraction of a second up to several minutes. With a few of these you can have one master timer operate all lights but have them come on in sequence.
Got a link?
 
Apart from concerns about the inrush current of the 18 contactor coils possibly being too much for a cheap timer, what about the effect on the feeder or service ?

18 contactors suggests a substantial load with possible risk of the feeder or main tipping if it all comes on at once.
I would therefore suggest the use of delay modules as suggested above. The exact delay is not that important provided that "all on at the same instant" is avoided.
 