Yes, a motor's impedance varies for many different reasons. Deenergized is one of them. A different mechanical load while energized is another. However, the case is presented here as having a specific coil (aka winding) impedance... so all other variables which change the winding impedance are irrelevant.
"all other variables which change the winding impedance are irrelevant", yes, yes, that was what I was trying to do. And therefore that was why I stated the problem as having a specific impedance. I was trying to eliminate variables but...... as the replies came in, I can see that there has been a "mission creep".
So let me change the question
I think he is asking the current magnitude difference/relationship between a wye and delta connected load of 10 Ohm per each coil (x 3)
not necessarily a motor
could be 3 10 Ohm heater coils
Yes, lets do 3 heater coils of 10 ohms each and they are connected to a 3 phase power supply. If I connect them in a delta or wye formation, I will get different coil voltages, different current flow amounts, different power ratings
Delta connected is a little different. Each winding is connected line-line, so we would have 480V/10 ohms = 48 amps per winding.
480V * 48 amps * 3 = 69120 watts.
This is much larger than the 22,470 for the wye connected motor, and if a wye motor could be reconnected as a delta, and have the same 480V applied, it would probably burn up really fast.
Yes, all this stuff can be quickly calced out using watts and ohms pies but the ohm pie has the ohm value and I was wondering how it would calc out depending on the wye or delta connection.
......(But then, the OP did say he's getting paid for it!)
Phil Corso
I get paid for some stuff that I do but this isn't one of them. This is purely theoretical. Im just trying to understand the math to a basic problem.
Let me simplify it this way:
3 independent heater coils of 10 ohms each
power supply is 3 phase 240 volt
ignore any reactance and just assume 100% power factor (remember simple theoretical not exact real life scenario)
How do you fill in the watts law and ohms law pies if connected wye.?
How do you fill in the watts law and ohms law pies if connected delta.?