Coil testing
pfactor2
United States
I have a Siemens Coil 120volt for 100amp lighting contractor. It requires momentary power to open and close contacts. Coil has two sets off poles that I assume would be moving the magnet in two different directions, but I have O resistance on one set off poles and correct resistance on the other set. Does one assume there is a short in the coil?
If you are measuring the coil contacts directly then you apparently have one coil with an open winding, thus defective
If you are measuring thru contacts, it may just be the normal holding contact open.
short
short
Does "O resistance" in your post mean zero resistance (a short) or Overload resistance, an open circuit?
0 meaning short.
Im assuming, i don't have any diagram or info for the coil, that,referring to the pic, the poles you see are two sets of coil connections within the contactor.
A shorted coil would typically show a blown fuse or control circuit damage somewhere. An open coil would show lack of operation.
The control circuit is momentary contact 120volt to close and open, three position on/on/off switch. The contractor is closed and will not open when 120volts is applied. No issues with control.
If you have zero resistance, I'd say the coil is shorted. It should draw high current when you try to energize it, unless it already did that at some point and took out some component in the control circuit.
Unless things have changed there are two things you might check before you install a new coil:
1. Be sure the armature moves freely. If it does not seat correctly the coil will burn out.
2. If its like the mechanically held contactors I've worked on in the past, the control circuit to the coil often goes thru a set of auxiliary contacts that opens and removes coil voltage once the contactor is set. make sure the contacts are working properly.
hard to tell without more information. coils are generally low resistance and can be close to zero ohms when measured with a common voltmeter.
best bet is to test it on your bench and see if it works by applying the appropriate voltage to the coil(s).
if it works great, if it does not work throw it away and buy a new one.
it is just basically a giant latch relay.