Coiled copper around terminated wire?

Status
Not open for further replies.

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
See attachment for what my question is about. (Picture was taken by one of my guys, I didn't see it in person.)

What is that? Is it a product? Or something done with bare wire by the electrician? What would be the reason for it?
 

Attachments

  • coiled wire terminations.jpg
    coiled wire terminations.jpg
    103.8 KB · Views: 5
See attachment for what my question is about. (Picture was taken by one of my guys, I didn't see it in person.)

What is that? Is it a product? Or something done with bare wire by the electrician? What would be the reason for it?

I would say done by the electrician because the lug was too large?
 
First for me, too. I couldn't help notice the precision of the coils. It's almost like they were machine made.
I think that it is sometimes used with fine stranded wire instead of using foil or a pin termination.
It also looks a little bit like something I might see on high temp wire in a heating appliance, but that does not seem to be the case here. Is this a breaker panel?
 
They don't look to large to me.

Really,
Think at this way.
How much space do those coils take then look at the space currently around the lug.

I bet this panel is a 200 amp and the lugs are rated 2 and above!
 
I would say done by the electrician because the lug was too large?
Similar to what I was thinking, but in the opposite direction. The lugs were too small, so instead of just clipping the strands (which is illegal), he attempted to avoid the technical violation by wrapping a strand or two nicely around the end, just after the insulation, but before the lug itself. You could easily tell by loosening the lugs and pulling the cable out, I bet the strands going in are fewer than what's in the cable.

Still a violation though. If the lug is too small for the bale, it's too small for the cable.

I see your point though too: the lugs would no go down SMALL enough for that cable, so he wrapped loose strands around the end to make the lug clamp down on it. As I look at it more, your scenario makes more sense in that the lug openings DO look too big.

As good as that looks, it's still a violation. Not suitable for the use.
 
Last edited:
Well, I guess I can take some pride in having come up with a true novelty. :D Thanks for all the responses so far.

The idea that the lugs are too large makes the most sense. It turns out that the panel label is partially ripped off, so it could be a 200A panel, and the feeder is on a 125A breaker. (It is an otherwise ordinary Eaton/CH breaker panel.) I believe the conductors are 2awg but it's possible they are a size off from that (i.e. 1awg or 3awg).

I have other reasons to believe this install was not above board, although it seems to have been done by someone knowledgeable who was cutting corners, rather than an amateur. I ended up not having time to call the customer today to ask questions, so maybe I'll have more to share later.

I'm also weirded out by how neat the coils are. That's what made me wonder if it was a legit product I didn't know about.
 
Really,
Think at this way.
How much space do those coils take then look at the space currently around the lug.

I bet this panel is a 200 amp and the lugs are rated 2 and above!
Most lugs used on a 200 or even 225 amp device will accept 6 AWG to 300 kcmil conductors.

Similar to what I was thinking, but in the opposite direction. The lugs were too small, so instead of just clipping the strands (which is illegal), he attempted to avoid the technical violation by wrapping a strand or two nicely around the end, just after the insulation, but before the lug itself. You could easily tell by loosening the lugs and pulling the cable out, I bet the strands going in are fewer than what's in the cable.

Still a violation though. If the lug is too small for the bale, it's too small for the cable.

I see your point though too: the lugs would no go down SMALL enough for that cable, so he wrapped loose strands around the end to make the lug clamp down on it. As I look at it more, your scenario makes more sense in that the lug openings DO look too big.

As good as that looks, it's still a violation. Not suitable for the use.
Sure looks to me like the conductor with insulation on it would fit into the lug or at least come very close to fitting.
 
It looks to me that the lug is sized fine with the wire. I think maybe the guy just took a long strand of wire and wrapped it around the wire bundle.

I don't see any violation here if so. Just a little unusual.

Maybe it is fine stranded wire? That would be a violation then even though the solution probably is a safe one.
 
It looks to me that the lug is sized fine with the wire. I think maybe the guy just took a long strand of wire and wrapped it around the wire bundle.

I don't see any violation here if so. Just a little unusual.

Maybe it is fine stranded wire? That would be a violation then even though the solution probably is a safe one.
So if the installer decided to use close fitting copper plumbing tubing instead of wrapping with that bare wire you would call that acceptable as well?

I agree it would likely work out pretty well but doesn't mean it is listed for use in that way.
 
Most lugs used on a 200 or even 225 amp device will accept 6 AWG to 300 kcmil conductors. ...

Unfortunately with the ripped panel label I can't confirm one way or the other what the lugs are listed for.

...

Maybe it is fine stranded wire? That would be a violation then even though the solution probably is a safe one.

I can tell from other pictures that it is not fine stranded wire. The strands are visible on the bottom side of the lugs in a couple photos. It seems the coiling doesn't go all the way through the lug, but I can't be sure how far it goes.
 
I hate wire ties in a panel. :happyyes:

haha. The left one is clipped a bit wonky, but neat install otherwise.

as for the coils around the primary lugs, obviously they are copper Heli-coils, used for stripped out wire. ;)

(if you dont get my sarcasm, it's okay. I have no idea what the pic is showing, just that it is creative. Probably wrong, but creative).
 
So if the installer decided to use close fitting copper plumbing tubing instead of wrapping with that bare wire you would call that acceptable as well?

I agree it would likely work out pretty well but doesn't mean it is listed for use in that way.

Note I did say it would be a violation, even though safe. There are actually some pieces of switchgear using bus bars made out of copper pipe that are listed.
 
Note I did say it would be a violation, even though safe. There are actually some pieces of switchgear using bus bars made out of copper pipe that are listed.
Note they are listed - and probably not a soft copper like some copper plumbing tubing is.
 