See attachment for what my question is about. (Picture was taken by one of my guys, I didn't see it in person.)
What is that? Is it a product? Or something done with bare wire by the electrician? What would be the reason for it?
That is weird. First time I've seen anything like that.
I would say done by the electrician because the lug was too large?
I think that it is sometimes used with fine stranded wire instead of using foil or a pin termination.First for me, too. I couldn't help notice the precision of the coils. It's almost like they were machine made.
They don't look to large to me.
Similar to what I was thinking, but in the opposite direction. The lugs were too small, so instead of just clipping the strands (which is illegal), he attempted to avoid the technical violation by wrapping a strand or two nicely around the end, just after the insulation, but before the lug itself. You could easily tell by loosening the lugs and pulling the cable out, I bet the strands going in are fewer than what's in the cable.I would say done by the electrician because the lug was too large?
Gotta give him an A for neatness and workmanship though. :thumbsup::roll:Looks nice, but its a new one for me.
I would say done by the electrician because the lug was too large?
Most lugs used on a 200 or even 225 amp device will accept 6 AWG to 300 kcmil conductors.Really,
Think at this way.
How much space do those coils take then look at the space currently around the lug.
I bet this panel is a 200 amp and the lugs are rated 2 and above!
Sure looks to me like the conductor with insulation on it would fit into the lug or at least come very close to fitting.Similar to what I was thinking, but in the opposite direction. The lugs were too small, so instead of just clipping the strands (which is illegal), he attempted to avoid the technical violation by wrapping a strand or two nicely around the end, just after the insulation, but before the lug itself. You could easily tell by loosening the lugs and pulling the cable out, I bet the strands going in are fewer than what's in the cable.
Still a violation though. If the lug is too small for the bale, it's too small for the cable.
I see your point though too: the lugs would no go down SMALL enough for that cable, so he wrapped loose strands around the end to make the lug clamp down on it. As I look at it more, your scenario makes more sense in that the lug openings DO look too big.
As good as that looks, it's still a violation. Not suitable for the use.
So if the installer decided to use close fitting copper plumbing tubing instead of wrapping with that bare wire you would call that acceptable as well?It looks to me that the lug is sized fine with the wire. I think maybe the guy just took a long strand of wire and wrapped it around the wire bundle.
I don't see any violation here if so. Just a little unusual.
Maybe it is fine stranded wire? That would be a violation then even though the solution probably is a safe one.
Most lugs used on a 200 or even 225 amp device will accept 6 AWG to 300 kcmil conductors. ...
...
Maybe it is fine stranded wire? That would be a violation then even though the solution probably is a safe one.
I hate wire ties in a panel. :happyyes:
So if the installer decided to use close fitting copper plumbing tubing instead of wrapping with that bare wire you would call that acceptable as well?
I agree it would likely work out pretty well but doesn't mean it is listed for use in that way.
Note they are listed - and probably not a soft copper like some copper plumbing tubing is.Note I did say it would be a violation, even though safe. There are actually some pieces of switchgear using bus bars made out of copper pipe that are listed.