CaptainKu
Member
- Location
- Kansas City
Hey all. I have a existing panel that arrived on site that is only rated 10KA SCCR. This is a 75HP air compressor. I was planning on running a 1/0 cable roughly 60feet to the panel but the short circuit at the end of the cable would still be 14KA. I have already trimmed down the calc as much as possible including using utility provided AFC instead of infinite bus. My thought was to extend the circuit to reduce the current but I would need to add about 100 feet. I am looking at the best way to install this cable and have a spare 24" tray I could install to loop the cable in ~4 times to get 100 feet added. I know looping in a circle could create additional inductance but would 4 loops of 1/0 cable in a 12' tray really cause a issue? Is there a better way to do this?