This is a utility term "Cold Load Pickup". After an outage, especially a winter outage, most of the utility loads are all set to start at once. All of the electric heat, water heaters, furnaces, lights, industrial machines, transformers, etc. will all try to turn on at one time as soon as the utility feeder breaker is closed.
These loads are usually scattered in time, turning off and on randomly so the inrush currents and operating current don?t all coincide. (Load diversity).
But when everything has been off for a while, all of the thermostats are calling for heat and all of the motors want to start at the same time.
The total inrush current and then the load current for the first few minutes may be greater than the normal feeder line overcurrent protection causing an unwanted trip on the utility feeder breaker. Modern relays have a feature that detects when load has been off for some programmable time and implements a temporary higher overload trip setting to allow cold load. Some relays can have their settings changed to Cold Load Pickup remotely by the system operator.
When designing overcurrent protection for utility feeders and substation, we have to consider the impact of cold load pickup and still protect the equipment.