In the NEC the meter disconnect allowed on the supply side of the service disconnect by 230.82(B) for cold sequence metering required by many utility companys on 480 volt services must be able to withstand the available fault current under 230.82(B)(1).
All the non-fusible disconnects are rated at 10,000 short-circuit amps max. So if the available fault current is over 10K then you have to you a fusible switch, correct?
Just looking for some feedback from those who have done such an installation...