J Joncampos3 Member Location San Antonio, Texas Occupation Electrician May 14, 2020 #1 Working in a commercial building, can you catch the cold water pipe and gas pipe anywhere in the building?
Working in a commercial building, can you catch the cold water pipe and gas pipe anywhere in the building?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician May 14, 2020 #2 If the water line qualifies as a grounding electrode, connection is done within 5 ft of entry to building. If not then bond anywhere Gas piping is considered bonded by egc with bc to equipment such as unit heaters
If the water line qualifies as a grounding electrode, connection is done within 5 ft of entry to building. If not then bond anywhere Gas piping is considered bonded by egc with bc to equipment such as unit heaters