Great stuff, thanks.
If the copper water lines in the crawlspace are not an electrode what are they called (in the code book)?
They are called copper water lines and they must be bonded. An electrode must have some contact with the earth
Around here they like for us to bond all of the water lines that are broken by pieces of plastic.
That is nuts.. you can tell them that I said so...lol If you are in the piedmont you can't be far from me... I have never heard of an inspector wanting that
If one were to go the copper water lines first, leap-frogging the pieces of plastic can one eventually end up at the water pipe electrode? There could be several breaks in the grounding electrode conductor. Or does the grounding electrode conductor need to be uncut?
The grounding electrode conductor must be uncut. Imo, it is easier to go to the metal pipe from the street then hit the copper lines. Those are called bonding jumpers and they don't need to be continuous.
If the metal water line entering the crawlspace from the street is something other than copper (galvanized or lead pipe) can the grounding electrode conductor be cut?
The code says metal water lines
250.52(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground
water pipe in direct contact with the earth for 3.0 m (10 ft) or
more (including any metal well casing bonded to the pipe) and
electrically continuous (or made electrically continuous by
bonding around insulating joints or insulating pipe) to the
points of connection of the grounding electrode conductor
and the bonding conductor(s) or jumper(s), if installed.
Thanks for the great help.