Usually engineers do this stuff for our jobs, but I thought I would try and figure it out, until the newest 250.66 stumped me.
Commercial building 4000A 3phase 480v main. The building was built in 1996, and we are doing a full gut and TI. Main switch board is energized so I havent opened the utility or main section to see if there are feeder cables (for sizing). Buss duct is used from the utility transformer into the building and into the back of the main.
The issue: the cold water bond is made in the core of the building at a restroom using 3/0 copper to 2" copper plumbing, unfortunately the water service (3" copper) enters the building about 150 feet away and completely on the opposite side of the building as the electric service (estimated 300'). I need to relocate this water bond to be with in 5' of the service entrance right? I initially thought I could run a 3/0 cu conductor, but a check of 250.66 now has "notes" for 1100kcmil or larger. These notes read like lawyer speak.
Can someone help me size my water bond? Code reference, and explanation? Or help me justify why I dont need to move it?