14.2.4 Identification by Color for Other Conductors.
14.2.4.1* Ungrounded circuit conductors that remain energized when the supply disconnecting means is in the off position shall be consistently applied as either ORANGE or YELLOW. These color identifications shall be strictly reserved for this application only.
Exception No. 1: Internal wiring on individual devices purchased completely wired.
Exception No. 2: Where the insulation used is not available in the colors required (e.g., high temperature insulation, chemically resistant insulation).
14.2.4.2 Where color is used for identification, the color shall be used throughout the length of the conductor either by the color of the insulation or by color markers.
Exception: Multiconductor cables shall be permitted to be permanently reidentified at the time of installation.
14.2.4.3 The use of other colors for the purpose of identification shall be as follows:
(1) BLACK for ungrounded line, load, and control conductors at line voltage
(2) RED for ungrounded ac control conductors at less than line voltage
(3) BLUE for ungrounded dc control conductors