I would like to know if there is anything in the code about using brown, orange and yellow wire on high voltage or at least phasing them.
Especially if those are larger conductors that are phase-taped, that's just ratty. How hard is it to purchase and use three additional colors of tape?Originally posted by brian john:
I recently saw a job with 480/277 3 phase 4 wire Black, Red, Blue same for the 208/120 3 phase 4 wire Black, Red , Blue AGHHHHHHHHHHHHHHHHHHHHHHHHHHHHHHHHH
If these are on branch circuits, there is a violation of 210.4(D).And right now that is not the case. I recently saw a job with 480/277 3 phase 4 wire Black, Red, Blue same for the 208/120 3 phase 4 wire Black, Red , Blue
The key seems to be "other approved means", the inspectors all seem good with this.210.4(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.
Don, I can certainly understand your feeling on this, so I guess I am glad you are not an inspector here.Originally posted by don_resqcapt19:
Bob,
I wouldn't accept that method as being in compliance with 210.4(D). To me the key wording in the section is "each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system". I don't see a color coded box cover as meeting this requirement.
Don
A couple of things I will point out, for single conductors we will use BOY Gray for 480, BRB White for 208. in fact a MA amendment requires the use of gray for neutrals of systems above 150 to ground and white for systems less than 150 to ground.each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means