i'm having trouble understanding why the C phase has to be tapped orange on the primary side of the switch gear ( for 120/240v three phase). can anyone please make it clear for me????? cause the NEC doesn't say anything about it.
And the HB commentary.110.15 High-Leg Marking.
On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded, only the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is orange in color or by other effective means. Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present.
The high leg is common on a 240/120-volt 3-phase, 4-wire delta system. It is typically designated as ?B phase.? The high-leg marking, which is required to be the color orange or other similar effective means, is intended to prevent problems due to the lack of complete standardization where metered and nonmetered equipment are installed in the same installation. Electricians should always test each phase relative to ground with suitable equipment to determine exactly where the high leg is located in the system.
Outside on the meter- C phase is highleg marked orange. On the inside the same wire is placed B phase and still marked orange.. POCO outside-- AHJ inside. Don't ask why: just do it ( don't think- it confuses the hired help)
	There's no rule on it. I guess it depends on whether you thing the entire exposed length needs to be marked, or just the ends near the terminations. I like the latter; it looks better.As far as color coding, is there a preferred method. Should you candy cane or tape entire conductor?